Small Cabin Forum / Cabin Construction / Ridge beam?
Author Message
dixie53
Member
# Posted: 24 Dec 2025 05:18pm
Reply 


I'll be building a small sleeping room in the spring, I want a vaulted ceiling, it will be 12x20 so the ridge beam will be 20 feet long, I'll use 10 foot 2x12s nailed and glued together, seams staggered, is 3 thicknesses enough? The rafters are less than 8 feet and it will have a metal roof. Can i get away with 2x10? I'm staying away from LVLs for cost savings. Thanks..

Atlincabin
Member
# Posted: 24 Dec 2025 06:07pm
Reply 


Hard to say without more info on potential loads - are you in snow country?

Brettny
Member
# Posted: 24 Dec 2025 07:48pm
Reply 


A sleeping loft? If your going to have a loft you dont need a ridge beam in that area, you can use a ridge board. In the vaulted ceiling area you may need a ridge beam but with such short rafters why not put a wall tie or two in and skip all the big lumber up high.

Is your foundation going to have a center support? If not a ridge beam wont work.

DRP
Member
# Posted: 24 Dec 2025 09:03pm - Edited by: DRP
Reply 


First, no, your homemade beam will not work as a beam, anywhere, anytime, joints must happen over support.

If the framing forms a triangle, then a non structural ridgeboard is fine. If the structure does not form a triangle, then a ridge beam, capable of supporting half the roof load is needed. 20' is a very long span. As BrettNY noted, each end of that beam needs holding up.

Some citations might help with understanding the requirements;

R802.3 Ridge.
A ridge board used to connect opposing rafters shall be not less than 1 inch (25 mm) nominal thickness and not less in depth than the cut end of the rafter. Where ceiling joist or rafter ties do not provide continuous ties across the structure as required by Section R802.5.2, the ridge shall be supported by a wall or ridge beam designed in accordance with accepted engineering practice and supported on each end by a wall or column.

R802.5 Ceiling joists.
Ceiling joists shall be continuous across the structure or securely joined where they meet over interior partitions in accordance with Section R802.5.2.1. Ceiling joists shall be fastened to the top plate in accordance with Table R602.3(1).

R802.5.2 Ceiling joist and rafter connections.
Where ceiling joists run parallel to rafters and are located in the bottom third of the rafter height, they shall be installed in accordance with Figure R802.4.5 and fastened to rafters in accordance with Table R802.5.2(1). Where the ceiling joists are installed above the bottom third of the rafter height, the ridge shall be designed as a beam in accordance with Section R802.3. Where ceiling joists do not run parallel to rafters, rafters shall be tied across the structure with a rafter tie in accordance with Section R802.5.2.2, or the ridge shall be designed as a beam in accordance with Section R802.3.