I spoke today to the spray foam guy: going to shoot for end of March to do the underside of the ceiling.

However, yesterday, I was speaking to the awesome contractor guy who did my driveway/pad. Here's what my plan was for the exterior of my cabin shell:

Board and batten shell, with boards, not with T-111 siding. I was going to go with foam board in between the batten strips. Then housewrap (or rainscreen????) over that. Then LP Smartside over that.

My guy said no, housewrap then insulation over that, then whatever siding.

Obviously it will still settle and dry some more, and we have been bombed with snow down there like everyone else. No construction is taking place yet...but I'm close! Considering getting some stuff done in a couple weeks when I have time off from work.

Thank you in advance as always!

DRP
Member
# Posted: 1 Feb 2026 06:21pm
Reply 


I'd say your guy is in line with this thinking;
https://buildingscience.com/documents/insights/bsi-001-the-perfect-wall

Brettny
Member
# Posted: 2 Feb 2026 10:49am
Reply 


Your putting foam board over the boards on the exterior and spraying in the studio bays?

Steve_S
Member
# Posted: 2 Feb 2026 11:59am
Reply 


Your contractor "guy" is correct. Do the walls, then wrap, then add the exterior 1" Foam Sheet, then strapping running VERTICALLY anchored into the studs/frame then Horizontally to attach your back boards to allowing for at least 1" space between boards then your battens to cover that gap. This provides an "air gap" thermal break which will not hold moisture and prevent heat/cold transfer from the outside to the inside.

If you do your Roof in a Cool-Roof method, you can connect that "air-gap" to your soffits so that as the roof warms, convection will pull the air up and vent it out on the Roofs Ridge Vent, which further prevents humidity or damp + keeps the structure neutral.

I designed my home using these methods and it's seriously efficient and having thermally broken walls/roof really prevents heat gain in summer & heat loss in winter... IE: My Radiant heating only runs 3 cycles of 2 hours within a 24hr period to maintain 25C/75F when it is -30C/-22F outside. In the summer when it is 40C/104F outside, the house never gets over 27C/80F and I no longer own an AC system.

A difference to your Board-Batten, I did Live Edge Cedar, using 8" cut cedar backboards with Live Edge Cedar face boards on the exterior. My roof is Forest Green Tin, so it does pretty good convection and run a full length Ridge Vent which pulls lot's of air up and out.
*NB: I am within a protected northern arboreal forest, which is primarily evergreens, and therefore my home blends in and is almost invisible as a result. The downside is that chipmunks & squirrels think it's a huge tree and run up along the sides sometimes.
** The roof seems thick, well it is, from the inside finish to the outside of the tin it is 13-1/2" thick, with PolyISO Sheet Insulation between the rafters.

Some photo's attached to help.
Cool Roof design
Cool Roof design
Batter Cross Batten (Roof & Wall)
Batter Cross Batten (Roof & Wall)
Cabin front - pre-porch
Cabin front - pre-porch


gcrank1
Moderator
# Posted: 2 Feb 2026 12:04pm
Reply 


If I had built our cabin again that is how I would want to do it!
And if my house burned down/blew away that is the kind of build I would use.

utherjorge
Member
# Posted: 3 Feb 2026 05:49pm
Reply 


OK, so as always...amazing help and ideas. The last time I did a thread, you all gave me ideas I hadn't considered and I've shifted my plans accordingly. It looks like yet again, what I thought I knew was incorrect.

So, the interior ceiling will be spray foamed. There's already a lay of some such (I'd have to dig up exactly what it is) under the metal roof, and that will be spray foamed.

My thought was to do rockwool in the interior spaces between studs. Plastic sheeting vapor barrier and then T&G on top for the interior walls.

If I do all that, for something that won't be a permanent home (12x16 cabin on skids) and has interior hear for when I need it...should I go through the trouble of putting that LP smartside stuff up for aesthetics? Or can I simply seal the cracks as needed and stain the exterior for aesthetics and let 'er rip?

Brettny
Member
# Posted: 3 Feb 2026 07:24pm
Reply 


What are you doing on the floor? All that with no solid floor insulation and the floor will still be as cold as the outside.

Honestly I wouldn't even bother with spray foam on a 12x16. Just use foam board and put it between thr studs and use canned foam around it.

utherjorge
Member
# Posted: 3 Feb 2026 09:06pm
Reply 


we have talked about jacking up the cabin to get under it to insulate, but I am not thrilled about that idea at all.

Like...the very opposite of being thrilled about an idea.

utherjorge
Member
# Posted: 8 Feb 2026 11:24am
Reply 


bumping for this question from before:

If I do all that, for something that won't be a permanent home (12x16 cabin on skids) and has interior hear for when I need it...should I go through the trouble of putting that LP smartside stuff up for aesthetics? Or can I simply seal the cracks as needed and stain the exterior for aesthetics and let 'er rip?

Brettny
Member
# Posted: 8 Feb 2026 05:13pm
Reply 


Personally I wouldnt re side it. I would however let it dry if its not kiln dried then cawlk every batten to the board and use a oil based stain on it.

We have a storage shed that was a temporary cabin with next to no insulation that was rough cut green board and batten. It's about 6yrs old. I stained it the first year. Some cracks opened up and you can see some light between the battens. I didn't cawlk everyone,just the worst. I wouldnt risk getting the insulation wet in yours for a few tubes of cawlk.

The oil based stain I used weathered superbly. It was TWP 1500 series.

utherjorge
Member
# Posted: 10 Feb 2026 08:32pm
Reply 


Brettny: what did you use for caulk? TWP being oil-based, what did you find worked.

I don't like the colors that much for the 1500 but the redwood can work if it has too lol

Brettny
Member
# Posted: 11 Feb 2026 05:58am
Reply 


I used a brown caulk home depot had duraflex or something. It was about $7 a tube. Not cheap but I have had cheap caulk crack and pull away even in interior situations. I didn't try to caulk the seams right after staining. Some I did well prior and most well after. I used a pump garden sprayer on my 10x14 shed bit it clogged and failed on the last wall. On my 20x32 1.5story cabin with t111, I used a spray gun that ran directly from a 5gal bucket. It was way faster. I also back brushed every bit of both buildings with a 6in stain brush.

My t1 11 siding needs a second coat and really could have used it 3yrs ago when I did it but it was fall and I was ready to move inside to insulate.

Tanner
Member
# Posted: 14 Feb 2026 01:06pm - Edited by: Tanner
Reply 


Here's my process for the exterior of our camp in New Brunswick: First, wrapped camp in house wrap against the sheathing. Next, spaced 1 inch strapping 16" on center, then filled that space with 1 inch insulation board (r3, I think). Then applied our hemlock board and batten that I had applied CWF-UV natural preservative before installing the sideing.




Walls are 2x6, r22 insulation between studs.
Gary

Tanner
Member
# Posted: 14 Feb 2026 01:11pm
Reply 


I installed the true 1" strapping to give better nailing for the board and batten
Gary

gcrank1
Moderator
# Posted: 14 Feb 2026 10:30pm
Reply 


Looks great!

utherjorge
Member
# Posted: 18 Feb 2026 11:25pm
Reply 


I'm not having any luck with caulk products.

TWP does not recommend any caulking products at all.

Different caulk companies also claim that you can't use their caulk with TWP since it is a deep-penetrating stain.

DRP
Member
# Posted: 19 Feb 2026 12:23pm
Reply 


That sounds like a stain problem rather than a caulk problem.
This is a full line supplier,
https://www.sashco.com/products/

utherjorge
Member
# Posted: 20 Feb 2026 07:09pm
Reply 


Sashco replied to me and told me that they cannot support some oil-based stains: I'm pasting their replies here:

Hello David,
I received your inquiry about Big Stretch compatibility with oil based stain on your project.

Big Stretch works with many types of oil base finishes. But it depends on what type of oil stain you use. If you use a film-forming oil, you should have no issues with adhesion. On the other hand, if you're using a non-drying oil product, your sealants are apt to fail.

Can you share with me which stain you've chosen?


I then replied TWP1500. To which I received:
David,
None of our sealants are compatible with TWP deep penetrating oil stains.
I suggest calling TWP to ask for their recommendation. If you have any additional questions for Sashco, please let me know.
And I hope your project goes well.


I had already asked TWP what they thought. Their reply was this:

Sorry, we do not have any caulk suggestions. It does need to be compatible with oil-based stains.

So! I went down to (up to?) the cabin today to fool around for a variety of reasons. One of them was to see what exactly I have going on when it comes to the battens. It will surprise none of you that you all are correct. Specifically, DRP, Steve_S, and Tanner appear to be the way I'll go. It will be super easy to pop off the battens. Then, housewrap, then go horizontal like you see with Tanner, and I'll reuse the vertical battens over the top of the horizontal strips/foam board and place the Smartside. It's definitely more work and almost certainly more money but I want to be able to enjoy it 4 seasons.

Brettny
Member
# Posted: 20 Feb 2026 07:22pm
Reply 


With wood siding if you don't go with a oil base deep penitrating stain your just treating the surface. Wood like to move and Crack. With any of that a surface coating is worthless. Just ask anyone who has a painted house in a moist climate.

However if your going to reside the place why not start finishing the interior and in the summer do the exterior? But then again its just a 12x16 cabin..could you just use 1-2in foam on the exterior and be happy with the interior like it is? No interior Insulation,drywall or wall coverings?

DRP
Member
# Posted: 20 Feb 2026 08:09pm
Reply 


It sounds like you already have TWP applied... my earlier point was, don't use a product that is incompatible with the world... but I sense you already have it on.

Have you taken a piece of scrap wood with this deep penetrating stain, and chopped a slice out of it after he fact? Most "deep penetrating oils" go in a cell or two deep. When the K-1, bunker crude, or diesel oil carrier/solvent of the day, flashes off and weathers a bit, caulk begins to adhere. Try some inconspicuous samples and see what sticks.

Uhh yeah, here we go;
https://www.twpstain.com/pdf/TWP_1500_Series_MSDS.pdf
Boiled linseed oils in spirits. Spirits and naptha, let it flash off and I'd try a polybutyl caulk... where needed. Think like a raindrop.

utherjorge
Member
# Posted: 21 Feb 2026 02:44pm
Reply 


Brettny: I actually was considering adding the windows in April and beyond as it'll be warmer, and I can each side, one at a time, to get things going. It's just studs at this time.

DRP: I have not yet applied anything, as the weather was definitely not conducive until this more recent week, and we're back to winter here already today.

DRP
Member
# Posted: 21 Feb 2026 06:21pm
Reply 


Ahh, there is what I mean by using a full line supplier. Use a product that has compatible caulks and stains.
I hear you weatherwise, we are on the rain/snow line tonight. The shop/sawmill melted out yesterday. I crawled under the worst hurt truck this afternoon. It has been a skating rink here. I look forward to spring!

utherjorge
Member
# Posted: 24 Feb 2026 02:38pm
Reply 


I had a great conversation with someone from the Weatherall company, who has a full line (DRP was right!) or products that will likely work. They are going to send me some stuff, and the overall reviews appear good.

A note: it's not oil based, it's latex, so my mileage my vary.

utherjorge
Member
# Posted: 1 Mar 2026 10:04am - Edited by: utherjorge
Reply 


So, the Weatherall package arrived in the mail Friday. I had inquired about their stuff, and they said they would send me some things, but I wasn't quite sure what they sent.

In short, I'm already very impressed with the company. Note...I didn't say product, because I haven't done anything with what I have received.

But: I received samples of caulk, their stain in the colors I had asked about in both the one-coat and two-coat styles, and the clear finish they expect you'll put over the stain.

I also got some sample cards with their colors of caulk and chinking.

I'm very happy with this so far, especially compared to curt and un-helpful replies from other products so far. I have a bundle of wood shingles I'll be trying this out on indoors in the coming couple of weeks.

[img]https://blogger.googleusercontent.com/img/b/R29vZ2xl/AVvXsEhcO-EVqM6uRCGtQG JnwUxF_uW44OFCEVUO_b_6xr_NaSfXDN1neJ9uKXMQbtjy3wqrHxQyLbKpmgcwmzeza70zUMQtEoR5AsB9DHZ KCLEGUavBnu15Qsfp3Pe-aHhAe-pmgNrulUSlCZRpnnM_spUsvaaqVl_c6gQU5wbFwLK3AVbpmm711qYBHAZc OYI/s320/weather1.jpg[/img]

[img]https://blogger.googleusercontent.com/img/b/R29vZ2xl/AVvXsEhX73iL0WLVmy48KL vhXSFEecORGdAIdshtoJnXa4-lQjoRJ7BfRmCQ4gOLYax4J8VtfM6f8k60icwdwBxBb9qETqdQstyDuCKdwT_ CR-yQxXpasDjYBLXQbcR0LmyGObKlMNWwLaHiAlTHgiTFWGA4kz8xRN7t5DKP1x5oEJdpVXDhSZcAIrZBCpH4 GFQ/s3181/weather2.jpg[/img]

EDITED TO ADD: No clue why uploading an address for pics is suddenly not working, so I uploaded the images.
weather1.jpg
weather1.jpg
weather2.jpg
weather2.jpg


utherjorge
Member
# Posted: 30 Mar 2026 04:25pm - Edited by: utherjorge
Reply 


OK! The ceiling has been spray foamed. Pics for attention below.

I asked the guy (who is a spray foam guy, not a batten guy) whether I should use a plastic sheet/vapor barrier if I use Rockwoll. He didn't think it was needed. In short, since I'll have HVAC and it's a small space, he didn't think I needed it...but he also wasn't sure. Thoughts?
ceiling1.jpg
ceiling1.jpg
ceiling2.jpg
ceiling2.jpg
ceiling3.jpg
ceiling3.jpg
ceiling4.jpg
ceiling4.jpg


DRP
Member
# Posted: 30 Mar 2026 06:36pm - Edited by: DRP
Reply 


We are in a mixed climate. No one here has used poly on a wall in 30 years.

https://www.youtube.com/watch?v=K6HR2ftXFss

utherjorge
Member
# Posted: 31 Mar 2026 12:44pm
Reply 


I skimmed that vid and will actually focus on it tonight.

I am eager to stain the outside with a sprayer to get an idea of where there are gaps I might not see. Moisture is down both inside and out, enough so I could spray right now, but some of the outside has already grayed, so I have to freshen it.

I mention any of that because I'm wondering if I'll need to do some sort of sealing inside so that moisture isn't coming in to hit the rockwool that will be in the wall, behind the shiplap panels. I'm going with stain and leaving the look as it is, and not insulating outside with foam board above a housewrap, under Hardie Board

DRP
Member
# Posted: 31 Mar 2026 02:50pm
Reply 


I'll just fill up your schedule for tonight
https://www.youtube.com/watch?v=U9IlMWrsE24

utherjorge
Member
# Posted: 8 Nov 2026 07:58am - Edited by: utherjorge
Reply 


Hello! As I finish the season out, I have more questions, but I'll ask those in other threads. I wanted to share a picture of where I am right now.

cabin front

First, I went and cleaned the wood; the Amish lumber had dried unevenly, and in some places got (perhaps?) moldy and green, and in other places looked great. I think it's a function of the weather, and how the wind comes up the hill, and what is actually the weather side. I used RMR-86 to brighten the whole thing up/remove yuck, and then rinsed it all well. Carrying 5 gallon pails of water from home was a good time.

I went with the Weatherall stain, in Amber. I stained it the once, and I was happy with the color.
https://www.weatherall.com/products/uv-guard-ii-exterior-wood-finish

I wanted to mimic this cabin design, as much as I wanted to, while modifying things. For instance, I don't care what their numbers are, the design doesn't match the plan dimensions and window sizes. No matter. I ordered the vertical window from Home Outlet and the sliding patio door came from a mobile home supply place, as the cabin is lower, height wise, that I could use a regular door for. That was an error on my end, but it's perfectly usable as is.

https://www.etsy.com/listing/1719523024/12x16-small-cabin-plans-200-sqft-shed

Trim all around will be painted black semi-gloss paint. There will be a deck in front here, in case you're wondering about that, too.

utherjorge
Member
# Posted: 8 Nov 2026 08:07am
Reply 


I should also include: I previously mentioned that I had the ceiling spray foamed.

Since I didn't think about insulating the underside when I first had the cabin built, I used 1/2 inch foam sheets above the floor and then 1/2 inch plywood on top. I know it's not much of a solution, but it has already made the cabin a) quieter, b) warmer, and there is no creaking as I walked around.

Allow me to also add I used SEMCO waterproofing everywhere, caulking the interior gaps then waterproofing over, and waterproofing the floor BEFORE putting the foam/plywood down.

I will be spray foaming the interior walls as well in the near future. Electric is now in and windows are (nearly) done so I can now foam.

Your reply