# Posted: 6 Nov 2026 01:09pm - Edited by: paulz
Reply
Does this go from 110 to 220 split phase US, like to run a 220v pump? That 220 socket doesn't look familiar.
|
|
DRP
Member
|
# Posted: 6 Nov 2026 05:49pm - Edited by: DRP
Reply
I bang nails and hire sparky for anything like this, so just a stab at it.
It looks like a double flat blade? If so look up a NEMA 6-15P, 15amps max@240V.
Looking at the posted specs it'll pull up to ~16.5 amps at 120V and produce about ~8.25 amps at 240V
I'm pretty sure our pump would let the magic smoke out of that if it is unprotected. Looking at my pump's specs, (put the stickers inside the breaker cover) 3/4 hp 6.8A 8 amps max at service factor. Motors take much more power to start. I wrote on the sticker 5500W but I don't recall ever plugging it into the genny.
|
|
paulz
Member
|
# Posted: 6 Nov 2026 06:54pm - Edited by: paulz
Reply
Yep that looks like it. Time to run to hardware store. Thanks! In the mean time I plugged it into 120. With the volt meter on the output terminals it measures 65 volts (neutral terminal zero) but it runs a drill fine. With spades in the 220 output it says 120. Hmm.
|
|
DRP
Member
|
# Posted: 6 Nov 2026 08:47pm - Edited by: DRP
Reply
You are "bucking" the 120 rather than "boosting" the 120V to 240V. Look up buck/boost transformer. It looks like you have the red rocker switch in the wrong position, push the left side. (Use the meter, don't cook a tool)
|
|
travellerw
Member
|
# Posted: 6 Nov 2026 09:18pm - Edited by: travellerw
Reply
Ok, I want to dispel some "electrical" information here!
The description of "Split phase" for Canada/USA is really misleading.
USA/Canada have line voltage transformed down to 240V. Then at the transformer we have a center tap (we call neutral). This makes 3 wires that are then fed to the residential property (a 4th wire comes from the grounding rod pounded in the ground). Measure between the 2 outside taps of the transformer and get 240V, measure between either outside tap and the neutral and get 120V. Not really "split phase", but they call the neutral the "split". The 120V side is the "split", the 240V side is not.
This is why any breaker in your panel that is 240, bridges both buss bars as those have 240V between them (no neutral wire). Most other breakers are just on one buss bar with a neutral.
Now with all that said, any of those step up/step down transformers on Amazon will take 120V (one hot + neutral) and step it up to 220/240 that will work with any 220/240V device. HOWEVER, since you have now stepped up the voltage (with some losses) you need to understand that you can only draw about 40% of the current your breaker is rated at on the 220/240V side. e.g if you have a 15A breaker on the 120V side, you can only draw about 6A from the transformer (actually less as you would break the 125% rule @ 6A).
Its better if you can just get a 240V pump and then pull 2 hots from the breaker panel. At that point you can draw the full current from your 240V breaker. However, if you don't have 240V available (maybe you have a 120V generator), then a transformer will work. BUT, there are considerations as you have now isolated the neutral from ground on the 240V side. The device you are running should have a reference to ground to be safe.
|
|
paulz
Member
|
# Posted: 6 Nov 2026 10:04pm - Edited by: paulz
Reply
Thanks guys. DRP you’re right, I flipped that switch and it reads correctly now. Why it says “input voltage” is odd, it only came with one 110 input cord.
Trav, I’m fooling with this for a 110 only generator as you mentioned. I ordered a 220 generator online but was told “can’t be delivered to California”’. Some EPA thing. So I’m hoping it will run my 220 well pump off a 110 genny i have already (have a 220 genny now on its last legs). And if it doesn't work im only out the 100 i paid. It will cost more in gas to drive to Reno and get a new 220 genny.
|
|
fusionsunsolar
Member
|
# Posted: 6 Nov 2026 10:52pm
Reply
One thing I'd check before trying the pump is the transformer's actual VA rating, not just the voltage: a well pump can draw a much larger surge at startup than its running amps suggest. Compare the pump nameplate and any starting-current data with both the transformer rating and the generator's continuous and surge ratings, since voltage sag can keep a motor from starting and overheat the transformer. Also, because the transformer may isolate the 240V side, don't assume its neutral/ground and GFCI arrangement is the same as a split-phase generator. If the manuals don't spell out a safe setup for that exact combination, an electrician can check it before you run it.
|
|
|